How do you determine if an outlet is part of a unidentified multi-wire branch circuit?
Here are three possible scenarios:
- There are 2 different hot wires (not a splice) and only 1 neutral wire connected to the outlet. This can be a single 240 V circuit, or it could be two 120 V circuits on a MWBC.
- Tracing the hot wire within the panelboard. Remove the cover of the panelboard and look for the cable or conduit where the circuit enters. If that circuit has more than one hot wire (connected to more than one breaker pole) then it could be a MWBC.
- Tracing the entire circuit. For the sake of updating outlets or other repairs, this is sometimes how MWBCs are discovered when they are not properly identified at the panel. By tracing an outlet to a splice where there are two differentseparate hot wire colors, this reveals the presence of a MWBC.
Note that measuring voltage is NOT a valid method. It is possible to have a MWBC installed wrong, such that the hot wires have zero voltage between them. This is why the other visual search methods are necessary.
Also note that turning off a single pole breaker identified for an outlet is not a reliable method. If the outlet is part of an unidentified MWBC, then there is a shared neutral involved and it will not get disconnected by the circuit breaker.
Does code say MWBCs need to be on double throw circuit breakers.
No, it is not required but sometimes still the easiest/best solution. The technical term for this is "common trip". NEC 240.15 provides an exception for MWBC if they are strictly used for line-to-neutral loads (120 V appliances only).
is it permissible to link CBs with that hole in the handle?
Yes, using a listed handle tie that is designed for that purpose. NEC 210.4(B) requires "a means that will simultaneously disconnect" the MWBC. This requirement has been in place for decades already.