I have a firman t07571, I followed this post to convert this generator to floating neutral.

I have a 200 amp main panel and a 125 amp sub panel. Generator breaker is installed in the main panel. I am just looking to turn on my well water pump and few lights and a refrigerator in the house to turn during a power outage.

I am using 50amp 2 pole breaker with interlock kit to back-feed the generator. Used a 6awg wire from generator inlet to main breaker panel with junction box, because wire i had was not long enough to go all the way to main panel, so added a junction box.

I turned off the main breaker, turned off back-feed 50amp breaker in the main panel, turned off all the other breakers, started the generator, hooked up the nema-14-50 plug to generator and other end of wire hooked up to generator inlet. Generator have 30 amp breaker, when I turn on the breaker on the generator, it trips immediately.

All the breakers on the main-panel are off including 50 amp generator backfeed breaker, but the when I turn on breaker on the generator (not breaker on the main panel, which is still off), generator breaker trips immediately.

enter image description here enter image description here enter image description here enter image description here enter image description here enter image description here

@Triplefault suggested to check the clamps of junction box, this is what i found in the picture below, i think this is what was causing the short, will fix and update herefixed the junction box and issue is solved.

enter image description here

I have a firman t07571, I followed this post to convert this generator to floating neutral.

I have a 200 amp main panel and a 125 amp sub panel. Generator breaker is installed in the main panel. I am just looking to turn on my well water pump and few lights and a refrigerator in the house to turn during a power outage.

I am using 50amp 2 pole breaker with interlock kit to back-feed the generator. Used a 6awg wire from generator inlet to main breaker panel with junction box, because wire i had was not long enough to go all the way to main panel, so added a junction box.

I turned off the main breaker, turned off back-feed 50amp breaker in the main panel, turned off all the other breakers, started the generator, hooked up the nema-14-50 plug to generator and other end of wire hooked up to generator inlet. Generator have 30 amp breaker, when I turn on the breaker on the generator, it trips immediately.

All the breakers on the main-panel are off including 50 amp generator backfeed breaker, but the when I turn on breaker on the generator (not breaker on the main panel, which is still off), generator breaker trips immediately.

enter image description here enter image description here enter image description here enter image description here enter image description here enter image description here

@Triplefault suggested to check the clamps of junction box, this is what i found in the picture below, i think this is what was causing the short, will fix and update here

enter image description here

I have a firman t07571, I followed this post to convert this generator to floating neutral.

I have a 200 amp main panel and a 125 amp sub panel. Generator breaker is installed in the main panel. I am just looking to turn on my well water pump and few lights and a refrigerator in the house to turn during a power outage.

I am using 50amp 2 pole breaker with interlock kit to back-feed the generator. Used a 6awg wire from generator inlet to main breaker panel with junction box, because wire i had was not long enough to go all the way to main panel, so added a junction box.

I turned off the main breaker, turned off back-feed 50amp breaker in the main panel, turned off all the other breakers, started the generator, hooked up the nema-14-50 plug to generator and other end of wire hooked up to generator inlet. Generator have 30 amp breaker, when I turn on the breaker on the generator, it trips immediately.

All the breakers on the main-panel are off including 50 amp generator backfeed breaker, but the when I turn on breaker on the generator (not breaker on the main panel, which is still off), generator breaker trips immediately.

enter image description here enter image description here enter image description here enter image description here enter image description here enter image description here

@Triplefault suggested to check the clamps of junction box, this is what i found in the picture below, fixed the junction box and issue is solved.

enter image description here

Became Hot Network Question
added 177 characters in body
Source Link
cody
  • 83
  • 5

I have a firman t07571, I followed this post to convert this generator to floating neutral.

I have a 200 amp main panel and a 125 amp sub panel. Generator breaker is installed in the main panel. I am just looking to turn on my well water pump and few lights and a refrigerator in the house to turn during a power outage.

I am using 50amp 2 pole breaker with interlock kit to back-feed the generator. Used a 6awg wire from generator inlet to main breaker panel with junction box, because wire i had was not long enough to go all the way to main panel, so added a junction box.

I turned off the main breaker, turned off back-feed 50amp breaker in the main panel, turned off all the other breakers, started the generator, hooked up the nema-14-50 plug to generator and other end of wire hooked up to generator inlet. Generator have 30 amp breaker, when I turn on the breaker on the generator, it trips immediately.

All the breakers on the main-panel are off including 50 amp generator backfeed breaker, but the when I turn on breaker on the generator (not breaker on the main panel, which is still off), generator breaker trips immediately.

enter image description here enter image description here enter image description here enter image description here enter image description here enter image description here  

@Triplefault suggested to check the clamps of junction box, this is what i found in the picture below, i think this is what was causing the short, will fix and update here

enter image description here

I have a firman t07571, I followed this post to convert this generator to floating neutral.

I have a 200 amp main panel and a 125 amp sub panel. Generator breaker is installed in the main panel. I am just looking to turn on my well water pump and few lights and a refrigerator in the house to turn during a power outage.

I am using 50amp 2 pole breaker with interlock kit to back-feed the generator. Used a 6awg wire from generator inlet to main breaker panel with junction box, because wire i had was not long enough to go all the way to main panel, so added a junction box.

I turned off the main breaker, turned off back-feed 50amp breaker in the main panel, turned off all the other breakers, started the generator, hooked up the nema-14-50 plug to generator and other end of wire hooked up to generator inlet. Generator have 30 amp breaker, when I turn on the breaker on the generator, it trips immediately.

All the breakers on the main-panel are off including 50 amp generator backfeed breaker, but the when I turn on breaker on the generator (not breaker on the main panel, which is still off), generator breaker trips immediately.

enter image description here enter image description here enter image description here enter image description here enter image description here enter image description here  enter image description here

I have a firman t07571, I followed this post to convert this generator to floating neutral.

I have a 200 amp main panel and a 125 amp sub panel. Generator breaker is installed in the main panel. I am just looking to turn on my well water pump and few lights and a refrigerator in the house to turn during a power outage.

I am using 50amp 2 pole breaker with interlock kit to back-feed the generator. Used a 6awg wire from generator inlet to main breaker panel with junction box, because wire i had was not long enough to go all the way to main panel, so added a junction box.

I turned off the main breaker, turned off back-feed 50amp breaker in the main panel, turned off all the other breakers, started the generator, hooked up the nema-14-50 plug to generator and other end of wire hooked up to generator inlet. Generator have 30 amp breaker, when I turn on the breaker on the generator, it trips immediately.

All the breakers on the main-panel are off including 50 amp generator backfeed breaker, but the when I turn on breaker on the generator (not breaker on the main panel, which is still off), generator breaker trips immediately.

enter image description here enter image description here enter image description here enter image description here enter image description here enter image description here

@Triplefault suggested to check the clamps of junction box, this is what i found in the picture below, i think this is what was causing the short, will fix and update here

enter image description here

Added picture of the wire causing short.
Source Link
cody
  • 83
  • 5

I have a firman t07571, I followed this post to convert this generator to floating neutral.

I have a 200 amp main panel and a 125 amp sub panel. Generator breaker is installed in the main panel. I am just looking to turn on my well water pump and few lights and a refrigerator in the house to turn during a power outage.

I am using 50amp 2 pole breaker with interlock kit to back-feed the generator. Used a 6awg wire from generator inlet to main breaker panel with junction box, because wire i had was not long enough to go all the way to main panel, so added a junction box.

I turned off the main breaker, turned off back-feed 50amp breaker in the main panel, turned off all the other breakers, started the generator, hooked up the nema-14-50 plug to generator and other end of wire hooked up to generator inlet. Generator have 30 amp breaker, when I turn on the breaker on the generator, it trips immediately.

All the breakers on the main-panel are off including 50 amp generator backfeed breaker, but the when I turn on breaker on the generator (not breaker on the main panel, which is still off), generator breaker trips immediately.

enter image description here enter image description here enter image description here enter image description here enter image description here enter image description here enter image description here enter image description here

I have a firman t07571, I followed this post to convert this generator to floating neutral.

I have a 200 amp main panel and a 125 amp sub panel. Generator breaker is installed in the main panel. I am just looking to turn on my well water pump and few lights and a refrigerator in the house to turn during a power outage.

I am using 50amp 2 pole breaker with interlock kit to back-feed the generator. Used a 6awg wire from generator inlet to main breaker panel with junction box, because wire i had was not long enough to go all the way to main panel, so added a junction box.

I turned off the main breaker, turned off back-feed 50amp breaker in the main panel, turned off all the other breakers, started the generator, hooked up the nema-14-50 plug to generator and other end of wire hooked up to generator inlet. Generator have 30 amp breaker, when I turn on the breaker on the generator, it trips immediately.

All the breakers on the main-panel are off including 50 amp generator backfeed breaker, but the when I turn on breaker on the generator (not breaker on the main panel, which is still off), generator breaker trips immediately.

enter image description here enter image description here enter image description here enter image description here enter image description here enter image description here enter image description here

I have a firman t07571, I followed this post to convert this generator to floating neutral.

I have a 200 amp main panel and a 125 amp sub panel. Generator breaker is installed in the main panel. I am just looking to turn on my well water pump and few lights and a refrigerator in the house to turn during a power outage.

I am using 50amp 2 pole breaker with interlock kit to back-feed the generator. Used a 6awg wire from generator inlet to main breaker panel with junction box, because wire i had was not long enough to go all the way to main panel, so added a junction box.

I turned off the main breaker, turned off back-feed 50amp breaker in the main panel, turned off all the other breakers, started the generator, hooked up the nema-14-50 plug to generator and other end of wire hooked up to generator inlet. Generator have 30 amp breaker, when I turn on the breaker on the generator, it trips immediately.

All the breakers on the main-panel are off including 50 amp generator backfeed breaker, but the when I turn on breaker on the generator (not breaker on the main panel, which is still off), generator breaker trips immediately.