I am switching my kitchen receptacle to a GFI; it has 3 wires. I'm pretty sure I have to break the bar between the two hot screws, thus making the top and bottom on a separate circuit. What is the reason for this way of wiring? The outlet is not feeding anything else, it's on its own circuit with a double pole 15amp breaker. Seems a little useless to me. The house was built in 1978.
-
3It sounds like you're describing a multi wire branch circuit. You cannot connect a normal GFCI receptacle as you're describing because you'll effectively have a shared neutral with one of the hots on the gfci. See How do I install a GFCI receptacle with two hot wires and common neutral? and Is this a “shared neutral” situation?BMitch– BMitch2013-09-15 00:23:45 +00:00Commented Sep 15, 2013 at 0:23
-
1What are the colors of the three wires? Do you know if the same circuit breaker currently controls both the upper and lower outlets?bib– bib2013-09-15 00:29:35 +00:00Commented Sep 15, 2013 at 0:29
-
2This almost sounds like the outlet under a kitchen sink, where there is a single duplex receptacle with one circuit for a dishwasher and a second circuit for a garbage disposal.Stefan Lasiewski– Stefan Lasiewski2013-09-15 00:55:02 +00:00Commented Sep 15, 2013 at 0:55