4

New outlet, red, black wire on one side one white on other and ground. Should the tab between the two load terminals be snapped off? It’s on a double 15 breaker. Using push click done receptacles. Could it be two separate circuits?

New contributor
Anna is a new contributor to this site. Take care in asking for clarification, commenting, and answering. Check out our Code of Conduct.
1
  • Needs clarification - is it a standard non-gfci outlet? North America? What type of terminal connection exactly? What is meant by “load terminals” in this case ( which terminals, why described as load)? Commented 9 hours ago

1 Answer 1

9

Red and black wires plus a double breaker is a good sign for a MWBC circuit. Often found in kitchens.

The tab should be broken off.

If you still have the old receptacle, you should find that it has the tab broken off.

As a comment mentioned, only break of tab on the hot side between the red and black.

3
  • 5
    You should be able to measure 240v between red and black to confirm, right? Commented yesterday
  • 8
    @Drise Yes if they are not connected together and tripping the breaker. Commented yesterday
  • 3
    Tab should be broken on the HOT SIDE ONLY for a MWBC!!! Commented 6 hours ago